Fuming!
- Russ-41
11 years 9 months ago - 11 years 9 months ago #137386
by Russ-41
Fuming! was created by Russ-41
Fortunately it's just me fuming and not my Jimny.
I ordered 10 meters of 1000+ strand 25mm² 170amp cable, it arrived today, and it's bloody copper coated aluminium (CCA) and not copper (OFC).
If someone could confirm my thoughts and reason for my slight anger - 25mm² CCA is good for 80Amps tops! where as your average 25mm² OFC will see 110Amp (and a little more on the finer 1000+ strand cables.)
The cable clearly states 170amp on the sheath, unless I'm mistaken, or they've invented a new element - someone perhaps less observant is going to end up with smoking hot cables and a potential fire if they use this stuff anywhere near its "rated" capacity.
Either that, or my £30 has bought me 10 meters of 99.9% silver core cable! :woohoo:
Last edit: 11 years 9 months ago by Russ-41.
11 years 9 months ago - 11 years 9 months ago #137406
by Rhinoman
The cable is specified as the number of amps that causes a particular rise in temperature so they could both be rated at 170A, its just that one will get hotter. Who manufactured the cable and what is the spec?
Last edit: 11 years 9 months ago by Rhinoman.
- Panama1
11 years 9 months ago #137413
by Panama1
Replied by Panama1 on topic Fuming!
The copper cladding will actually help some at the higher frequencies and even some small effect at 60 cycles (darn little to none). On a D.C. circuit, the copper is purely decorative. My engineering books give a wire size of 00 or 67.4 mm squared for a working load of 175 amps for copper wire. This load will heat the wire to 75 centigrade. My tables show 75 amps working load for the cable you bought - at 75 centigrade. If this is for a winch, 0 (53mm) copper will work just fine- it will carry 170 amps at 90 degrees cent. Meanwhile, it just may be silver!
- Russ-41
11 years 9 months ago #137461
by Russ-41
Replied by Russ-41 on topic Fuming!
Thanks Panama1,
I used 90°C as the allowable operating temperature this way the ambient temperature coefficient drops to 0.82 ish, from 0.75 for 50°C ambient (the temperature correction factor is probably below the ampacity table in your eng. book)
The cable will have a 100amp slow fuse so that's the limit here.
The cable has no brand, and no marks on the sheath saying 170amp, that was just the sellers stock photo I think. The cable is just marked as "high grade 4AWG" power cable - so it's not even 25mm, its 21mm!! They miss sold this from just about every angle they could.
For comedy effect, I calculated (roughly) what temperature 21mm CCA would reach at 170amp - 255°C
(My degree is mechanical engineering, so we've only covered basic electric DC and 3 phase AC real/imaginary power inductance impedance etc. - probably enough for this scenario but as this isn't something I do every day I posted on here to see if anyone else could help.)
- Russ-41
11 years 9 months ago - 11 years 9 months ago #137579
by Russ-41
Refund sorted with the seller, when I pointed out it was 4AWG and no where near 25mm^2, and asked at what temperature their supplier rated it at 170A I think that highlighted perhaps the data sheet, didn't match the supplied cable, they've removed it from ebay now
The other sellers who have the same stuff at similar prices have confirmed it to be OFC so I'll grab some of that
Time to create page: 0.084 seconds